A 2 horsepower, 120-volt, single-phase motor has a nameplate full-load current of 24 Amperes. What is the maximum rating of a time-delay fuse permitted for short-circuit and ground-fault protection for this motor, assuming no special conditions?

Master LevelšŸ“‹ NEC 430.52(C)(1) and Table 430.52, NEC 240.6(A)Motor
Circuit Diagram
Motor Branch Circuit — NEC Article 430 PANEL 480V 3Φ DISC 430.109 ≄115% FLC OCPD Breaker 430.52 ≤250% FLC 125% FLC Conductors 430.22 OL 430.32 ≤125% FLC M Motor Sizing Summary (per NEC 430): 1. FLC from Table 430.248 (single-phase) or 430.250 (3-phase) 2. Conductors ≄ 125% Ɨ FLC [430.22] 3. OCPD ≤ 250% Ɨ FLC (inverse-time breaker) [430.52 Table] Key NEC References: 430.6 — Use nameplate for overloads, table FLC for OCPD/conductors 430.22 — Conductor sizing (125% of largest motor FLC) 430.52 — OCPD maximum ratings (Table 430.52) 430.32 — Overload protection (≤125% FLC for SF ≄1.15)
A

30 Amperes

B

40 Amperes

C

50 Amperes

D

60 Amperes

Explanation & Direct Citation

The correct answer is located in the National Electrical Code Section XXX.XX(Y)(Z). Lorem ipsum dolor sit amet, consectetur adipiscing elit. Sed do eiusmod tempor incididunt ut labore et dolore magna aliqua. Ut enim ad minim veniam, quis nostrud exercitation ullamco laboris nisi ut aliquip ex ea commodo consequat.